Fronius Hybrid with Modbus TCP

Einklappen
X
 
  • Zeit
  • Anzeigen
Alles löschen
neue Beiträge
  • Tico
    Lox Guru
    • 31.08.2016
    • 1035

    #31
    LoxMunich - You're welcome.

    1. Ignore the missing numbers. You haven't missed anything. When creating the wiki, I excluded some of my own data fields that filled 07 to 10 that were not relevent for the .loxone file.

    2. Look at the Fronius Smart Meter sensor 'W' = Flow to/from grid - kW (Positive=Import, Negative=Export). Run this sensor into a State Block value AI1. Run the Battery State of Charge 'ChaState' into the same State Block AI2.

    Set up the argument when AI1 ≤ (minimum charging value) and AI2 ≥ 98, then output value 1. Use the value 1 for whatever switching mechanism you need. The battery varies between 98-100% in the fully charged state. You could make AI2 = 100, but car charging would then stop unnecessarily.

    3. Same logic for the Ohmpilot. You need to decide which device has the 1st priority - car charging or Ohmpilot. Then if one device is charging/heating and there's still grid outflow, start the other.
    Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

    Kommentar

    • LoxMunich
      Extension Master
      • 29.12.2016
      • 146

      #32
      Thanks, I will try this the next days.

      One other question: the sensor values in the .Loxone file seem to be different to the sensor values in the .XML files.
      E.G.
      Klicke auf die Grafik für eine vergrößerte Ansicht

Name: from imported xml.png
Ansichten: 1347
Größe: 68,6 KB
ID: 261671Klicke auf die Grafik für eine vergrößerte Ansicht

Name: from.Loxone.png
Ansichten: 1478
Größe: 76,9 KB
ID: 261672
      left the imported .xml / right the .Loxone sample file


      What is the latest version / which should I use?

      Kommentar

      • Tico
        Lox Guru
        • 31.08.2016
        • 1035

        #33
        Thanks for pointing that out. The .Loxone file is the most recently updated - use it.

        I think I'll delete the .xml files in the wiki. I seem to remember that they were required in previous Config versions when loading up the .Loxone file. Perhaps someone can confirm whether the .Loxone file brings all sensors/actuators across without the underlying xml data? I can't test that on my existing installation.

        https://www.loxwiki.eu/display/LOXEN...ith+Modbus+TCP
        Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

        Kommentar

        • LoxMunich
          Extension Master
          • 29.12.2016
          • 146

          #34
          You have to import the .xml files

          Only the memory flag / Merker are added automatically if you just "select all" elements from the .Loxone page and copy & paste it into a new project page.
          Neither the sensors nor the actors within the Modbusserver and even not the virtual inputs / outputs are there

          Kommentar


          • Tico
            Tico kommentierte
            Kommentar bearbeiten
            That's jogged my memory now when copying into a new project page. I'll get around to updating the xml files in due course.
        • renezs
          Extension Master
          • 01.07.2016
          • 133

          #35
          Hello,

          does anyone have the modbus register data for the new smart meter TS65a-3. It seems to bee different with the template from here. The communication works but there are or not the right value.

          Kommentar

          • Tico
            Lox Guru
            • 31.08.2016
            • 1035

            #36
            What type of inverter do you have and what is the firmware version? Have you checked that your inverter is updated to the latest firmware?
            Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

            Kommentar

            • renezs
              Extension Master
              • 01.07.2016
              • 133

              #37
              I have the Symo Gen24 Plus 8.0 and the firmware 1.9.7-0. This should be the actual

              Kommentar

              • Tico
                Lox Guru
                • 31.08.2016
                • 1035

                #38
                Ok, you might need to contact Fronius direct. As the first user here of the Gen24, congrats! It will be interesting to find out how much more responsive it is than the Hybrid.

                I found the following details in the TS 65A-3 instruction manual regarding firmware. Not much help unfortunately.
                Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

                Kommentar

                • renezs
                  Extension Master
                  • 01.07.2016
                  • 133

                  #39
                  Thanks,

                  this is what i have find too :-).
                  I have sent the questions to fronius. Let's see what's the answer.

                  Kommentar


                  • Tico
                    Tico kommentierte
                    Kommentar bearbeiten
                    One difference I did read with the new smart meter is the Modbus device address -

                    Fronius Smart Meter 63A-3 has factory value 240.
                    Fronius Smart Meter TS 65A-3 has factory value 1.
                • renezs
                  Extension Master
                  • 01.07.2016
                  • 133

                  #40
                  at time i have some values from the inverter. But maybe not the right.
                  The modbus device adress for the smart meter youn can choose over the webpage of the inverter. The preset her was 200.

                  Kommentar

                  • renezs
                    Extension Master
                    • 01.07.2016
                    • 133

                    #41
                    i have one other problem
                    on Pp i have connected my actual production (AC_Power) but on AQp is notting shown, also not on the visualisation.

                    Klicke auf die Grafik für eine vergrößerte Ansicht  Name: inverter.JPG Ansichten: 0 Größe: 36,1 KB ID: 267160
                    Zuletzt geändert von renezs; 27.09.2020, 20:10.

                    Kommentar


                    • Gast
                      Gast kommentierte
                      Kommentar bearbeiten
                      Hi there

                      I have a system with 2 pcs. Sym Gen24, each with its own Byd battery pack, and 1 pc. Symo 20. We have just started the system and are going to connect it to Loxone. We have some challenges with getting the right data from both inverter and Smartmeter, I have been on fronius website to find the modbus tables but without success. Have you had any challenges with your connection to Gen24 and the batteries.
                  • Tico
                    Lox Guru
                    • 31.08.2016
                    • 1035

                    #42
                    For info, the Vendor Operating Codes are as follows (from a question raised earlier in the thread) -

                    Klicke auf die Grafik für eine vergrößerte Ansicht

Name: Vendor Operating Codes.png
Ansichten: 924
Größe: 56,7 KB
ID: 272574

                    The State Value is set to 0 for regularly occuring (normal operating) status. The Filtered Error codes are passed onto the AIe input of the Loxone Energy Monitor.
                    Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

                    Kommentar

                    • Gast

                      #43
                      Wie kann ich über Modbus auf die Zielgröße am Zählpunkt zugreifen?
                      Dazu finde ich keinen Register.

                      _____________________________


                      Klicke auf die Grafik für eine vergrößerte Ansicht

Name: Energiemanagement  Fronius Hybrid.JPG
Ansichten: 852
Größe: 30,3 KB
ID: 296210

                      Kommentar

                      • Tico
                        Lox Guru
                        • 31.08.2016
                        • 1035

                        #44
                        Google Translate says -
                        Gast - How can I access the target size at the metering point via Modbus?
                        I can't find a register for that.


                        I assume you mean the minimum battery reserve (paragraph 3 in the index)?

                        https://www.loxwiki.eu/display/LOXEN...batteryreserve.
                        Ich spreche kein Deutsch. Gib Google Translate die Schuld, wenn ich unverständlich bin.

                        Kommentar

                        • Gast

                          #45
                          No, I mean the target value at the metering point.
                          Thanks