I have a Loxone based system with a ModBus extension. I bought an Inepro PRO-380-Mod PM to capture my power consumption. As it has a Modbus interface and as I have the Modbus Extension for Loxone it seemed quite obvious to capture the data with Loxone.
That's it for the idea, but the execution is not that easy. Wiring the PM to Loxone extension is not a big deal, 2x0,4 twisted wire, it is only about 1m from the PM so distance is not an issue.
For some reason I can not reach the PM through Loxone.

For the PM I have a very detailed manual, all the primary settings like, Modbus adress, baud rate, parity, stop bits are set correctly. In the manual I have the register addresses, and data types for reading out the data. Like this:
Eg: Total Active Power register address is 2080 , and 4 data blocks (2*32 bit register?), and data type is floating point with Big Endian byete order.
I set up Loxone Modbus device (analoge senzors) like this:
And despite this, after the polling I do not have any value from this sensor.

It saying : invalid receive - length.... (the ide after that is exetnsion address).
Do anybody any clue where I went wrong, and how could I enforce this two device to communicate with each other? I tried to use different data types but no luck with them. Any help is much appreciated.